[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-3-26 14:14 编辑
9 P( ]5 E: V' \1 n$ Z' y) q9 l9 L# Q- t
Two  cutler –hammer advantage  starters are  doing the same thing:
  |' [" Q! I; q3 M% G' [ After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
: J6 E! j! ~9 m( ~4 @+ [: _It is a cycle.
( g" D) w9 B9 p& P
, L# b' [3 d# f- G( @6 u7 t, X4 mWe isolate the network control and use the local start and stop only, the problem remains.: G% e3 J- k4 k& i, m2 O
Swap one of the defective buckets with a good one, the new bucket works fine.
: p7 A0 Z$ F- L5 hThe problem should be inside the bucket.
3 _+ E) Z& o. M5 u/ X# V4 o, t
( }% x2 m" r: T1 a' oWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.. J, o; s3 u% l& `' \
Use a terminating screw divers to push in the contactor, it will not seal either.
  H9 h) }# R4 l% GConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
2 v8 u' x' n  ?$ [- [* ]9 O7 B  }) E' q. H9 j* x/ h
The next thing we can think of  is the coil, we took the coil out to have a close look.: w% z: K3 o: A& x# b
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.- U6 R" ]1 V! Y4 W
It is getting better  this time, we have 7-8 times of running before it quit working.
. b7 l: m% K; s2 C! S
$ D. {  a( d/ @# ]8 \; TThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
* i: f* a' R$ o1 q& h+ m; ^2 J" Q' N# z* y
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
4 f) r2 b, S% P5 H* [% q7 F$ _' y; p; x1 W- t" c& ]
中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
4 t3 n$ P) ~$ A' U/ k+ ^Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 2 N) O  I. q# e% x% }" q7 P+ Y
也想到这一点,不过这是新装的设备。
- \1 z' |6 u' g- b检查过触点没问题。