Two cutler –hammer advantage starters are doing the same thing:
|' [" Q! I; q3 M% G' [ After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
: J6 E! j! ~9 m( ~4 @+ [: _It is a cycle.
( g" D) w9 B9 p& P
, L# b' [3 d# f- G( @6 u7 t, X4 mWe isolate the network control and use the local start and stop only, the problem remains.: G% e3 J- k4 k& i, m2 O
Swap one of the defective buckets with a good one, the new bucket works fine.
: p7 A0 Z$ F- L5 hThe problem should be inside the bucket.
3 _+ E) Z& o. M5 u/ X# V4 o, t
( }% x2 m" r: T1 a' oWhen the problem happened, we observed that the contactor has a pulling action but will not seal.. J, o; s3 u% l& `' \
Use a terminating screw divers to push in the contactor, it will not seal either.
H9 h) }# R4 l% GConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
2 v8 u' x' n ?$ [- [* ]9 O7 B }) E' q. H9 j* x/ h
The next thing we can think of is the coil, we took the coil out to have a close look.: w% z: K3 o: A& x# b
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.- U6 R" ]1 V! Y4 W
It is getting better this time, we have 7-8 times of running before it quit working.
. b7 l: m% K; s2 C! S
$ D. { a( d/ @# ]8 \; TThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
* i: f* a' R$ o1 q& h+ m; ^2 J" Q' N# z* y
Do you guys have any input on this issue? |
|