0 D+ q" @+ q* z/ v, A/ rTwo cutler –hammer advantage starters are doing the same thing:
4 z) [: d' L. w6 {$ a0 D) b After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. \ o4 k8 S6 x0 t7 q4 c$ d) F
It is a cycle.
N8 J! n% F% m0 ~: ?8 e( `
( j# K# e) X4 g7 K6 jWe isolate the network control and use the local start and stop only, the problem remains.6 |: b% c) {* U7 p5 p
Swap one of the defective buckets with a good one, the new bucket works fine.
) K0 Q3 C% E% e& C) n2 DThe problem should be inside the bucket., i0 z! \2 V& e a+ [0 j5 [" M C
2 k" Z3 A; D4 m: Q2 d
When the problem happened, we observed that the contactor has a pulling action but will not seal.! U! P% |1 D6 t t+ \: H
Use a terminating screw divers to push in the contactor, it will not seal either.6 h# M3 C" _, L5 n- W, \* V
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
* E' ~/ L5 V1 s: a' n# g% T7 F+ k) t/ R C
The next thing we can think of is the coil, we took the coil out to have a close look./ j+ n& ]9 \- m9 }
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.4 Q4 C! L1 {! {) l+ [! s& V
It is getting better this time, we have 7-8 times of running before it quit working. ' z, u! F* b8 q! v& i7 _
1 O Y/ q3 f( u! o) ?The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 3 h% V, Z* y* n% l
0 j! w; S) K2 A5 M: Z9 ]$ @7 y
Do you guys have any input on this issue? |
|