Two  cutler –hammer advantage  starters are  doing the same thing:  e" X# C% T! l8 Q5 g$ H1 V. ~
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again. 5 Y5 C/ G; A7 w9 l
It is a cycle.
* x' W+ ^2 \: y
( n0 d% }3 t/ a0 o. kWe isolate the network control and use the local start and stop only, the problem remains./ x; |7 o1 J3 I* S* l) @! J
Swap one of the defective buckets with a good one, the new bucket works fine.
& G2 `, O  Q# t2 k# ?The problem should be inside the bucket.( q0 I% R/ r% d8 N& m
% }3 t; z" D( S2 `- A5 c# r# @: {
When the problem happened, we observed that  the contactor has a pulling action but will not seal.8 h" K6 ]! u/ I! I# L6 F
Use a terminating screw divers to push in the contactor, it will not seal either.1 `& \5 X' ^" m  p1 `/ ]0 q
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.7 p% W% N8 M# Z. G( L- m
" s0 l$ f7 u. l4 e" G$ Y, j
The next thing we can think of  is the coil, we took the coil out to have a close look.2 W8 _4 w8 f0 o
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
( G. D: ]  L8 e It is getting better  this time, we have 7-8 times of running before it quit working. ' k9 D- i; Y0 F0 E4 x

4 s! _9 r* x( X# @- S2 F8 ^The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. + k& u" m( s0 F6 I4 M+ g+ g; @& w

9 I7 @1 ?, |! TDo you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
理袁律师事务所
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 + a+ v/ X9 C6 O. }% V

1 s  W7 I2 \! ?/ q0 d0 L8 i; z中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.1 W: t+ D/ u% J, d% y9 y2 q
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
大型搬家
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
% ]- T; h0 G7 A3 x9 k也想到这一点,不过这是新装的设备。
  O9 l: L2 k; [" W( _. I5 }7 d! [检查过触点没问题。