We all know that if you want to change the rotation of a three phase AC motor.1 @3 {9 _5 S7 z2 A. V5 Z$ Q& D
Just swap any of the two phase leads.8 S& x' B$ \0 @& j' M" Z
But for VFD application you need to do the swap after the inverter.: l" g7 o; m" f
If you swap the leads before the inverter, it will not work.
Yes, Good point. 7 {; i. j$ v+ s$ R* n0 j8 E2 a" G- H3 d0 Z) Z8 E$ ?
As the principal of the VFD works, bascially from AC to DC, then DC to AC. j0 ?6 n1 {7 B1 K; w
4 a7 V7 o8 e1 }( Y
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all. 1 j& l. Y' M5 S" V. O7 Y8 O Y' t2 a4 w/ n1 ^2 q* ]1 w* J$ R* y
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.