) x$ {. ?; E, \4 H0 fTwo  cutler –hammer advantage  starters are  doing the same thing:
9 Z8 J7 b6 n. E: ^5 f/ h After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
3 B# _. V1 B9 BIt is a cycle.
8 e3 P7 [8 x, Z2 Q2 T8 m
* b: y" _4 w  k; pWe isolate the network control and use the local start and stop only, the problem remains.8 k5 t6 d2 c8 @! {7 u
Swap one of the defective buckets with a good one, the new bucket works fine.: o/ g1 K7 j3 T; I
The problem should be inside the bucket./ V& Z* b* P/ X! z, C5 @. q$ m

; r+ L8 p% ^" \' WWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.
/ I( ]' N, k" A- NUse a terminating screw divers to push in the contactor, it will not seal either.
: o$ J( ]" q  P6 x  LConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
+ b6 x/ n- N# Z. X. C! z7 w. g/ v8 U7 o; P' k! ~* t9 A$ D. m; C8 [2 @
The next thing we can think of  is the coil, we took the coil out to have a close look.0 w$ E7 T' G1 q3 _
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
- \0 |( {& D+ J3 H It is getting better  this time, we have 7-8 times of running before it quit working.
6 `4 K8 H7 _/ h2 h7 s0 ]7 `  s7 H% k. H7 g  O: z9 }% x
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. & L1 Z7 R* |5 v+ B, {5 _+ A) Y
7 S! {! h' O7 p' H. k8 k. s
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
, r5 i; d3 P3 k) j9 M/ K5 G. E, P
中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
) w/ Z- R# `% V; ASince your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 % k1 E, A' j: A- s4 Q+ F
也想到这一点,不过这是新装的设备。7 ?/ l; y  [3 s: K- f
检查过触点没问题。