$ C+ e. q0 y& x9 A- Y0 lTwo cutler –hammer advantage starters are doing the same thing:
0 V3 B1 W) n/ G0 |. z" _, O After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
3 v; a8 b0 h6 R3 h3 vIt is a cycle.2 C1 ?7 Y( V8 k- ~8 }: [
- R; q1 B D5 b- v2 k
We isolate the network control and use the local start and stop only, the problem remains./ l$ b; `' [$ t- |2 h# S
Swap one of the defective buckets with a good one, the new bucket works fine.* Y# d: P( [( c; x
The problem should be inside the bucket.
0 h0 J8 d- \7 X4 B4 w4 l# b8 g x1 J8 H1 K1 c0 }. K! x
When the problem happened, we observed that the contactor has a pulling action but will not seal.! [' i+ A4 k8 Z+ l! ]
Use a terminating screw divers to push in the contactor, it will not seal either.4 }. U/ e# [' R, \- X& R {
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.. X$ a( C4 Y! z. e. ]; x$ v; E
% B) o9 Z, ]5 r K+ h& C
The next thing we can think of is the coil, we took the coil out to have a close look.
! @; q3 W& s U; v5 P/ b) L' VThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.. k0 F% m M* S0 x+ w
It is getting better this time, we have 7-8 times of running before it quit working.
: K1 \" }: o/ G0 z7 |0 r" ~1 o4 R
2 [; g& `1 B2 v0 t+ e6 `% LThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 4 m% B1 X2 e$ F$ a
& B' {) @7 B2 l
Do you guys have any input on this issue? |
|