We all know that if you want to change the rotation of a three  phase AC motor.
5 `) g% ~8 v: L% F$ |! [Just swap any of the two phase leads.7 ?1 J6 ^* k% `( S
But for VFD application you need to do the swap after the inverter.
3 s  z+ L# W* j4 D6 wIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
' t. s# [3 ~8 w9 [' H5 A5 n3 K! D
As the principal of the VFD works, bascially from AC to DC, then DC to AC.
$ c# ?. E" Q0 r( j- D; n$ T& }; k+ |1 x* E+ N( l, D
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
% A8 T$ Z$ t) O/ }& i. ?; k( S2 @5 L
; f% R( h3 f3 \The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.