本帖最后由 td456 于 2010-4-14 12:28 编辑 ; @5 h  E* L0 f3 \( Y" z9 h5 L

: s! n  q' c' U. d, e/ qWe all know that if you want to change the rotation of a three  phase AC motor.9 e3 ~& Z" X# C& E2 F
Just swap any of the two phase leads.' n, l4 y9 K  x" P, k
But for VFD application you need to do the swap after the inverter.8 k! W$ i7 f' Z  f
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
6 t* S& ?4 u6 h* @2 y, v6 w( w+ c3 `  f) r
As the principal of the VFD works, bascially from AC to DC, then DC to AC. * R  Z5 m6 {2 r" N  m$ a

$ e, d  Y5 A  L8 U4 j3 zThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all." b2 r+ K8 z2 X( _6 w

% P' \& ^/ T! yThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.