[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
( `1 V9 ]+ `. c* _* W: v! A9 ?! a" E% ~3 Q( d' {+ w9 z; J
We all know that if you want to change the rotation of a three  phase AC motor.5 |, {7 N) O0 a) o, O) A
Just swap any of the two phase leads.* r% E# K% ^- U- p3 [8 |) ^& Q- G0 i
But for VFD application you need to do the swap after the inverter.
- ]% q4 _' d6 u9 h) vIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
7 S! X2 Z1 P, u- Y6 J
: T1 ]; O- F0 t) P# i! g6 ^As the principal of the VFD works, bascially from AC to DC, then DC to AC.
, h5 i% v4 }; [" x' Z$ ], _0 D  X! A# B4 x6 p* l- i9 ^4 C
The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.) d. N9 J* E8 v+ b0 A3 F! K

& U; `" L8 z. x) g  S, m5 _The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.